Electric Baseboard Heaters

Status
Not open for further replies.

chris1971

Senior Member
Location
Usa
Could someone explain the pros and cons of installing standard electric baseboard heat compared to oil filled electric baseboard heat?
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
Could someone explain the pros and cons of installing standard electric baseboard heat compared to oil filled electric baseboard heat?
I believe the oil filled baseboard heaters will maintain the heat longer after the power is off to the unit.
 

iwire

Moderator
Staff member
Location
Massachusetts
Watts are watts and electric heaters without fans are all 100% efficient.


I believe the advantage is more even heating, as Dennis mentioned they cool slower but they also heat slower, this will keep the temp in the room more consistent.
 

peter d

Senior Member
Location
New England
There is no advantage to using the oil filled BB heaters if you use a triac switching (non mechanical) thermostat. The electronic stats much more accurately control the temperature which renders the oil filled feature not necessary.
 

electricmanscott

Senior Member
Location
Boston, MA
I have two oil filled baseboard units. The get just as hot as any other electric baseboard heat.

They are also far more expensive to buy then standard electric baseboard heat.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
I believe the oil filled baseboard heaters will maintain the heat longer after the power is off to the unit.
Yes, but they also take longer to heat up when reenergized. Therefore, over time, the two types should cost the same to run. It's also true that the room temperature should vary less between cycles with the greater mass of the oil-filled heaters.

At home, we keep our HVAC blower set to 'on' instead of 'auto' so the room temperatures don't vary as much between cycles. Otherwise, the rooms can vary by 5-6 degrees while the hallway where the thermostat is only varies by 1-2 degrees.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
A couple of years ago, the fiance of a good customer asked me to price installing expensive oil-filled permanent baseboard heaters throughout her condo, because she felt she was paying too much to heat with her HVAC system.

I went there, did a quick look around the unit and a better look around her attic space. Then I explained how a one-time expense to reduce heat loss would benefit her more than a new way to pay forever to replace the escaping heat.

There were loose duct connections, sloppy and missing insulation, and the furnace needed a good tune-up, as evidenced by the yellow flame. I recommended an HVAC technician, an insulation specialist, and to look into new windows.
 

kbsparky

Senior Member
Location
Delmarva, USA
Depending on the manufacturer's instructions, you may be permitted to install the oil-filled units under receptacle outlets.

Straight heat-element types usually are restricted to open wall spaces only.
 