He didn't say what the configuration is but of the four heaters he has 2-1500 watt heaters which cannot be on a 15 amp circuit.Why not (2) 15A 240V circuits? 14/2?
He didn't say what the configuration is but of the four heaters he has 2-1500 watt heaters which cannot be on a 15 amp circuit.Why not (2) 15A 240V circuits? 14/2?
I am in Massachusetts and i am installing 4 baseboard electric heaters in a finished basement 2- 6ft 240v 1500w and 2-240 1000w do each electric baseboard need a designated circuit i know normally they do not but in mass there is a bunch of regulations on heating now was looking in 424 but couldn't find anything Defina native
He didn't say what the configuration is but of the four heaters he has 2-1500 watt heaters which cannot be on a 15 amp circuit.
Why not (2) 15A 240V circuits? 14/2?
Correct. Hopefully the OP returns to fill in the blanks but to your point:If he pulled two 15 amp circuits a 1000 watt and 1500 watt heater would have to share a circuit . He can’t put both 1500 watt heaters on a 15 amp circuit
Correct. Hopefully the OP returns to fill in the blanks but to your point:
1500+1500=3000/240=12.5*125%=15.625 amps minimum circuit size.
i wanted to do a 30 i guess it depends what the terminals are rated for correct?
Related question not to hijack the thread. I always thought that baseboard heaters required a two-pole thermostat with an off position to use as a disconnect.
I have seen a lot of Honeywell digital electric heat thermostats with only 2 wires, so it is a single pole thermostat.
I always thought if single pole thermostats were used that the breakers need permeant locking mechanism.