I have read article 695 and NFPA 20 (several times)
Still confused on a few things.
Fire pump Service
695.3 A (3) Dedicated feeder. Can someone give me an example of what is meant by this section since this is one of the acceptable methods of providing power?
If I use 695.3 (1) (Tap section on switchboard ahead of the main) the fire pump feed is a service and will need a disconnect with overcurrent protection per 230.70 & 230.90. After I tap the service in the separate section and come out of the tap overhead I need to have a service disconnect located at the tap, no?
In what type of scenario of a service to a fire pump can you use 695.4 (A) Direct Connection? If it is a service it needs a service disconnect and OCP again to comply with 230.70 and 230.90. So not a direct connection. I realize 695.4 (B) allows this but why have (A) at all?
Thanks for any replies.
Still confused on a few things.
Fire pump Service
695.3 A (3) Dedicated feeder. Can someone give me an example of what is meant by this section since this is one of the acceptable methods of providing power?
If I use 695.3 (1) (Tap section on switchboard ahead of the main) the fire pump feed is a service and will need a disconnect with overcurrent protection per 230.70 & 230.90. After I tap the service in the separate section and come out of the tap overhead I need to have a service disconnect located at the tap, no?
In what type of scenario of a service to a fire pump can you use 695.4 (A) Direct Connection? If it is a service it needs a service disconnect and OCP again to comply with 230.70 and 230.90. So not a direct connection. I realize 695.4 (B) allows this but why have (A) at all?
Thanks for any replies.