Sparky2791
Senior Member
- Location
- Northeast, PA
- Occupation
- Electrical Design
Thanks Jim. I have read that many times and missed it. No OCPD no need to rate for locked rotor Amps. What are your thought on a fire pump service fed directly from a pad mount (second service) to a CT cabinet. From the CT cabinet to an disconnect disconnect w/o OCP from the disconnect to the fire pump Overhead thru the building in 2 hour fire rated circuit protective system. Without the OCP in the disconnect is it a feeder and no longer service entrance conductors. Does 90.3 allow non compliance with 230.90 in said disconnect?Actually it is quite clear.
The last sentence of NEC 2014 Article 695.4(B)(2)(a)(1) says:
" The requirement to carry locked-rotor currents indefinitely shall not apply to conductors or devices other than overcurrent devices in the fire pump motor circuit(s)."