Electric furnace disconnect
fisherelectric
Northern Va
Got called to a house remodel job today where the GC said the furnace disconnect was "throwing sparks" and the heat wasn't working. Found a heat pump system with 20 kw back-up heat in the air handler. The original ('70s) furnace circuit was #2 Al sec w/ 100amp OCP run to a Zinsco 125amp 8/16 mlo load center. Then (I assume) 2 50 amp breakers feeding 2 pieces of #6Cu sec run to the furnace. One piece of #6 was burned up on the ends, the breaker was missing and it was curled up in the load center. The other #6 was on a 50amp breaker that was smoked. The bus bar where the both breakers had been was badly burnt. The hex screws were missing from the main lug terminations so the #2 sec had been arcing in the lugs with the furnace load. In addition, 2 120v circuits had been added to this loadcenter with no neutral present, using the sec ground to make them work. It looked like it had been that way for a long time.
I told the GC the whole mess needed to be replaced with 2 new circuits from the service and 2 new 60 amp disconnects and run new circuits for the 120volt loads. My question is was the original install compliant... the 125a MLO with 2 breakers feeding the furnace as disconnects, leaving space for hacks to add circuits with no neutral present or should it have had 2 disconnects to begin with? The furnace calls for 2 60amp circuits (MOP) and has supplementary breakers factory installed. Under the '05 here.
My guess is no load calcs were ever done when the heating system was installed. 20kw of heat strips is already 83 amps of a 100a service. THat sure don't leave much for anything else.
I told the GC the whole mess needed to be replaced with 2 new circuits from the service and 2 new 60 amp disconnects and run new circuits for the 120volt loads. My question is was the original install compliant... the 125a MLO with 2 breakers feeding the furnace as disconnects said:
supplementary breakers factory installed[/U]. Under the '05 here.
Yes, I think it was compliant.
Regarding fixing this, with breakers in the furnace, I do not think you need additional disconnects.