Just started my own contracting business and have a question for you 'experienced contractors.'
Connecting a residential 10 KW/240 Volt furnance and would like to know what type of wiring method you guys use. I was going to use 2 runs of 6/2 w ground NM-B. NEC ampacity table shows 55 amps for #6 NM-B. The branch circuit conductors need to be 60 amps based on 48 amps X 1.25. Can I still use the #6 NM-B?
The linear distance from the service panel to the breakers inside the furnace is 40 feet. I was going to staple the cable to the lower edges of the floor joists in the unfinished basement.
Thanks,
Mike
Connecting a residential 10 KW/240 Volt furnance and would like to know what type of wiring method you guys use. I was going to use 2 runs of 6/2 w ground NM-B. NEC ampacity table shows 55 amps for #6 NM-B. The branch circuit conductors need to be 60 amps based on 48 amps X 1.25. Can I still use the #6 NM-B?