jerjwillelec
- Nevada, IA
- Master Electrician
I have a customer complaining about the electric heat in her apartment. She claims when the (in line) thermostat is set on 60, that the room heats up to around 70 - 75. She also claims her electric bill has gone up compared to previous winters.
This room is approximately 300 square ft. There is a 240 volt 2500 watt baseboard heater on one wall and a 240 volt 500 watt baseboard heater on the other wall.
I have replaced the thermostat (even though I didn't 100% feel that was the problem) and it continues to do the same. The t-stat is a Mears M601 single line break 22 amp rated. I realize this style of t-stat will have a varying range of degree fluctuation, but I wouldn't expect it to be more than a degree or two (maybe 3).
The 2500 watt heater element has 25.5 ohms of resistance (cool). The 500 watt heater element has 123.5 ohms of resistance (cool). The supply voltage to both heaters is 247 volts. By doing the math, this says the 2500 watt heater is only producing 2402 watts of heat and the 500 watt heater producing 494 watts of heat.
My question is this... do electric baseboard heaters loose efficiency over time creating a "hot spot" and causing the electric bill to go up or is this all in her head?