When two equal load are wired in series and supplied by twice one unit's rated voltage, they will each see approximately their rated voltage, about half the total, and operate as they should.Dissimilar loads in series causes dissimilar voltages across each load, inversely proportionate to each load's resistance. The larger heater will cause the small one to see the most voltage.
However, two dissimilar loads in series, if supplied by twice one unit's rated voltage, will each see a different voltage, often destroying the one with the higher resistance due to over-voltage.
This is exactly what happens when a neutral opens. The line-to-line voltage remains the same, but whichever half of the line-to-neutral loads has less load will be subject to higher voltage.