goldstar
Senior Member
- Location
- New Jersey
- Occupation
- Electrical Contractor
We recently rewired a kitchen where the specs for the gas cooktop/electric oven (combination unit) called for a 30 amp line for the oven section. At the final install the appliance came pre-wired with a 4', 50 amp cord & plug. The installation manual called for a 50 amp receptacle yet still only required a 30 amp circuit. I did not have the 50 amp receptacle with me but did have both the 30 amp receptacle and cord/plug set. I changed out the 50 amp cord with the 30 amp and installed the 30 amp receptacle. Is there a code violation here or can these units be converted in the field as I did ?
Thanks in advance,
Phil
Thanks in advance,
Phil