Thats why I threw in the 100 years "or so".
I would still be interested in knowing how a difference in potential could exist between the washer and dryer due to the three wire installation.
Would the washing machine missing a ground?
How could this be blamed on the dryer??
The dryer would be connedted to the grounded conductor which is...grounded
The grounded conductor is a current carrying conductor. If it opens, and you get between the frame of the dryer (if bonded to the neutral) and the washer, you become part of the neutral path.