roger Moderator Staff member Location Fl Occupation Retired Electrician Oct 15, 2010 #2 See article 220. Roger
jxofaltrds Retired ESI Location Mike P. Columbus Ohio Occupation Creator Oct 15, 2010 #3 eddybee said: how do I fiquire the feeder load demand for 4 ranges in a home? Click to expand... I think that this is a Home Inspector question. But I will be nice. Table 220.55. If this home has 4 ranges read 220.55 first.
eddybee said: how do I fiquire the feeder load demand for 4 ranges in a home? Click to expand... I think that this is a Home Inspector question. But I will be nice. Table 220.55. If this home has 4 ranges read 220.55 first.