Neither the nec, nfpa, ubc or ibc provides a definition for "electrical equipment room" or "electric room". Thanks bwyllie for the nfpa 13 info. We have the 2007 nfpa 13, it is article 8-15.10 in lieu of 4-13.10 but it states the same, & seems to be applicable to the OP. We also spoke to the ahj building official today. Their local ruling also requires compliance with nfpa 13, as well as equipment rooms with fire pumps shall have a 2 hour rating, & certain building occupancy classifications i.e. where the electric room wall is common with an exit corridor on the other side of the electric room wall, H7 occupancies, etc...
Michael