Electric room

Status
Not open for further replies.

codequestion

Banned
Location
MD, USA
I have 75kva transformer ceiling hung in electric room. To comply nec 450.13. Do electric rooms have suspended ceilings or just structural ceilings?

Sent from my SM-G935U using Tapatalk
 
I know you cant install it in hallow space or closed space but electric room they dont have hallow or closed space right? They just have structural ceiling, nothing closed no?

Sent from my SM-G935U using Tapatalk

When you say "Structural ceiling", I'm assuming you mean its above the transformer. That should be fine.

In other words, if you can look up and see the transformer, then yes, it should be fine.

If you look up and see the ceiling, and the transformer is above that, then its a problem.
 
When you say "Structural ceiling", I'm assuming you mean its above the transformer. That should be fine.

In other words, if you can look up and see the transformer, then yes, it should be fine.

If you look up and see the ceiling, and the transformer is above that, then its a problem.
Every electrical I went to only had structural ceiling. Did not see any susoended ceiling.

The question is the following: in an electrical room is their only structural ceiling? Thats how electrical rooms are built in the USA?

Sent from my SM-G935U using Tapatalk
 
Last edited:
The question is the following: in an electrical room is their only structural ceiling? Thats how electrical rooms are built in the USA?

Sent from my SM-G935U using Tapatalk

In the US there is no one way to construct an electrical room. The NEC is silent on the issue of ceilings as far as types permitted. I will say that I can't remember the last time I was in an electrical room that had any kind of drop ceiling or inaccessible ceiling space in which wire, cable, or raceway were run.
 
In the US there is no one way to construct an electrical room. The NEC is silent on the issue of ceilings as far as types permitted. I will say that I can't remember the last time I was in an electrical room that had any kind of drop ceiling or inaccessible ceiling space in which wire, cable, or raceway were run.
Maybe a PI inregards to types of ceiling permitted electrical room or who cares about that?

Sent from my SM-G935U using Tapatalk
 
Request NEC to put tyoes of ceiling permitted in an electrical room.

Sent from my SM-G935U using Tapatalk

Is there a safety reason for this? The NEC isn't intended to be a design manual (or so they say). Unless you think there is an electrical safety issue involved I don't see a need for any intervention on the topic. Whether it's a metal deck with concrete on top, a wood joist ceiling, or a concrete waffle slab I don't see why the NEC should care.
 