wanted to know if there was a specific distance that an electric meter should be from a gas main on the exterior of a home? any help on this topic would be greatly appreciated


edited by moderator to remove e-mail address. If you need to contact someone privately please use the message function.

[ October 14, 2004, 07:19 AM: Message edited by: don_resqcapt19 ]
 
Re: electric services

Not in the NEC, as long as you don't violate 110.26.

Indoors, our local utility requires a 3 foot seperation.
 
Re: electric services

It's based on the indivdual utility, if you ask me. JCPL in New Jersey says 10 feet, but other might say 12' or 15'. Definitely check the utility! :)


Lady :)
 
Re: electric services

Charlie's reference, NFPA 54 (2002 Edition) is the minimum I'd recommend.

5.7.2.3 Gas meters shall be located at least 3 ft (0.9 m) from sources of ignition.
A 3 Ft, Division 2 radius at valves and flanges is common for natural gas delivered at 100psi or less in open air. A smaller radius would take some very extensive, probably fruitless, gas dispersion analysis. Depending on local prevailing winds(long periods of relative calm, for example), up to 5 ft may be reasonable. Anything over 5 ft is probably for "warm fuzzies;" but a utility may have experienced a specific incident that, in their minds, justifies a greater distance.
 