ELECTRIC WATER HEATER

ING23

Member
Location
Las Vegas
Occupation
Site Survey Tech
I am trying to understand how add this water heater load to my All electric Residential Load calc. This Electric Tankless water heater use 3 x 40A breakers. Brand new house , I suppose it is been review by the Engineers but this Water heater is bumping up my numbers way over my main breaker . Any Idea how a brand new house was designed this way?
 

Attachments

  • tyuio.jpg
    tyuio.jpg
    857.5 KB · Views: 67

suemarkp

Senior Member
Location
Kent, WA
Occupation
Retired Engineer
Looks like 4 40 amp breakers, not 3. What is the KW rating if the heater? It will go into the load Calc at 40% of that, but even that is going to add about 50 amps or so on its own. Maybe it fits, but show your load calc. Many people end up not liking tankless electric water heaters because of flickering lights and they still may not be powerful enough if two showers are going at once.
 

LarryFine

Master Electrician Electric Contractor Richmond VA
Location
Henrico County, VA
Occupation
Electrical Contractor
In my opinion, those four 40a breakers should be in their own 200a panel, perhaps with one or two other line-to-line loads. I have upped a 200a to 320/400a just for a tankless with the same 4 x 40s.
 
Location
NE (9.06 miles @5.9 Degrees from Winged Horses)
Occupation
EC - retired
I just read a paper on these water heaters and the POCOs supply. The case under study required a doubling of the transformer feeding the house. 25 to 50 KVA. VD was still noticeable, but livable. The paper suggested that POCOs are adjusting what they will provide and will add costs to compensate for theses WH demands.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I am trying to understand how add this water heater load to my All electric Residential Load calc. This Electric Tankless water heater use 3 x 40A breakers. Brand new house , I suppose it is been review by the Engineers but this Water heater is bumping up my numbers way over my main breaker . Any Idea how a brand new house was designed this way?
What method are you using for calculating the load? It is pretty amazing what the nec will allow on a 200 amp service.
 

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
... Any Idea how a brand new house was designed this way?

No. Or rather, I do have one idea: someone didn't know what the @#$%! they were doing.

I'd almost go so far as to say these things should be banned. Heat pump water heaters are more energy efficient.
 

Little Bill

Moderator
Staff member
Location
Tennessee NEC:2017
Occupation
Semi-Retired Electrician
That whole panel is a mess. Why would anyone start off fresh with too few spaces for the loads? The panel is using quads and twins right off the bat. Looks like a 30 space panel, and should have been a 40. Actually, with the four 40's, it should have been a 400A service with two panels.
 

ramsy

Roger Ruhle dba NoFixNoPay
Location
LA basin, CA
Occupation
Service Electrician 2020 NEC
someone didn't know what the @#$%! they were doing.
Op is in Las Vegas, which was on 2017 NEC, until 3/23/23 adoption of 2021 IBC (using 2020 NEC).


Las Vegas appears to adopt codes without amendments, including AFCI's, not found in Op's photo of fusebox.

Notice labels for kit/bath breakers to GFCI outlets, but Bedroom breakers not labeled to AFCI outlets.

Unqualified & deliberate construction defect are typically ignored during occupancy, especially remodel outlets, when furnishings may block access to inspection points.

Virgin real-estate may be unmolested, but plenty of track home defects pass inspection, and nothing avoids tax assessors & AHJ's more than property sales.

Custom home builders may be the last bastion of good construction.
 
Last edited:

jaggedben

Senior Member
Location
Northern California
Occupation
Solar and Energy Storage Installer
Op is in Las Vegas, which was on 2017 NEC, until 3/23/23 adoption of 2021 IBC (using 2020 NEC).

...[etc]...

My point was simply that a competent person doesn't install a 150A water heater on a 200A service for a single family home. You get a different water heater or a different size service.

Another way to put it is that most people don't bother to actually do load calcs for new single family homes, and just spec a 200A service. And most of the time that works out fine. But not with an electric on demand water heater.

I agree that the other details suggest that this wasn't the only aspect of the electrical that was rushed and sloppy.
 

Dennis Alwon

Moderator
Staff member
Location
Chapel Hill, NC
Occupation
Retired Electrical Contractor
I just did a load calc using 32 amps x4 for the water heater or 30,720 watts. I used 4,000 sq.ft added the typical range, dryer, microwave, dw, etc. I used 10000 watts for the a/c unit. I came up with 183 amps using the optional cal and 238 using the standard
 

ING23

Member
Location
Las Vegas
Occupation
Site Survey Tech
Yes , this is in Henderson NV, the OP photo is not an isolated house, this is a Town house and like this , could be 60 or maybe more house with the same water heater. This is the first time I see a Tankless water heater like this one on a dwelling unit. I understand all your concerns, but my question was .. how to deal with this kind of appliance on a Load Calc.
 