Calrissian45
Member
- Location
- Southern California
- Occupation
- Electrical Engineer
My employer has an electrical acceptance test plan that measures the voltages at the panelboard, transformer, and furthest outlet to verify that the voltage drops are within the maximum recommended 3% for branch circuits and 5% for branch and feeder circuits combined. I was tasked to update it and as I was looking it over I realized that the voltage drop is determined by the load and this test plan is measuring no load conditions, which seems kind of worthless. So I'm curious if anyone has any insight on what to test under no load conditions to verify that the electrical power system was installed correctly. We can't test under load conditions (without simulating the load) since the loads are installed by others after we leave the job site.