Is it acceptable to mount an electrical box on pallet racking that is bolted to the floor? I could have the conduit strapped to the wall behind the rack and then bend it to the front. Thanks in advance.
I would see a problem with it, if the electrical equipment is subjected to physical damage.
When you're using a forklift to shift pallets in and out of the racks, there's plenty of chance for damage to happen.
I've seen plenty of pallet racks with electrical added to them, whether it be for receptacles, lights, or something specific (like battery charging or drum heaters). You absolutely MUST take pallet movement into account, or the wires and pipe will be all over the floor within days.
Placement is key, with the electrical stuff typically being mounted behind the horizontal cross pieces. I've also seen boxes placed between stout metal protective 'wings' that are attached to the framing.
A common way to mount the stuff is with the use of beam clamps and mineralacs. One does want to be careful about drilling holes into the framing.
Even when the framing is bolted to the floor and 'permanent,' you want to allow for flexing where the wiring method transitions from the wall to the racking. Those racks move about quite a bit as pallets are pushed into them- even if the feet are bolted down.
A final consideration is whether there are sprinklers in the racks. That can affect your design Remember- the sprinklers are also just as likely to 'go off' when hit by a pallet - and you don't want the water collecting in your boxes.
Why aren?t you? It may be a grey area in some situations, but if you have a rack that houses an electrical box?where pallets will be stacked?using a folk lift, or thrown-on by some hired hand. Why would this seem grey?? Seems subjected to me!!! Also, read my question. I asked what is a pallet rack?which means I need clarity. Seems the OP needs lucidity as well!!I'm not sure what you are getting at here. Which part of the install would be a problem if subject to damage?
Actually subject to physical damage is such a grey area. I mean can you install ANYTHING where you know it's going to be damaged?
I believe some common sense plays a roll when installing electrical. So, suppose this happens is a good question to ask yourself!!! Asking opens the door to evaluating—which is a good thing!!! Lets not knock people for being rational.Oddly, we can sit here all day long with, "Suppose this happened?" etc. It doesn't matter what we think , unless you, by chance are the AHJ for this situation. Every post here brings you back to, "The code does not prohibit it, ask you local inspector." Throwing out something like the sprinklers is just getting too involved. Heck there are sprinklers in my building, maybe I should install in use covers and GFCI's on my receptacles.