S safetyscott New member Sep 12, 2006 #1 Is there an NEC requirement to prohibits the use of electrical boxes with knockouts from being installed on walls or machinery?
Is there an NEC requirement to prohibits the use of electrical boxes with knockouts from being installed on walls or machinery?
T triphase Senior Member Sep 12, 2006 #2 No. As long as the unused KO's are still intact or effectively closed. 110.12(A) 05' NEC
celtic Senior Member Location NJ Sep 13, 2006 #3 safetyscott said: Is there an NEC requirement to prohibits the use of electrical boxes with knockouts from being installed on walls or machinery? Click to expand... No, but their are restrictions if certain instances - wet areas require a 3R rating. What is your application?
safetyscott said: Is there an NEC requirement to prohibits the use of electrical boxes with knockouts from being installed on walls or machinery? Click to expand... No, but their are restrictions if certain instances - wet areas require a 3R rating. What is your application?