E enricom Member Location south carolina Aug 26, 2021 #1 electrical box with some flex wire secured to conduit that has low voltage network wiring, think its a NEC issue NEC, Article 800-52? Attachments dropzip.jpg 1 MB · Views: 9
electrical box with some flex wire secured to conduit that has low voltage network wiring, think its a NEC issue NEC, Article 800-52?
E enricom Member Location south carolina Aug 26, 2021 #2 is that flex allowed to not be secured beyond 10 ft so if run vertically?
don_resqcapt19 Moderator Staff member Location Illinois Occupation retired electrician Aug 26, 2021 #3 300.11(C) says raceways can't be used to support other raceways or cables.