All,
My questions relate to installation of cables in directionally drilled conduits. For those of you who are unfamiliar with the technique it basically a horizontal drilling method in which a bit is pushed underground and conduit (usually HDPE - High Density Polyethelene) is pulled back in the borehole and used as a sleeve.
In our area, most of the time directional drilling is used for water, gas lines, and utility primary/secondary cable. The sleeves are usually roll out HDPE and vary in size from 3" to 18" which are fused to join the lengths. Our questions relate to the installation of electrical cables in these sleeves. The HDPE has no U/L listing as electrical conduit. The utility usually install their primary and secondary cables since they are not concerned with the NEC and U/L.
1) We are wondering if we install a cable or cable assembly (i.e. 3 conductor with ground shielded cable assembly similar to Coreflex) which is rated for direct burial can we install it inside the HDPE sleeve since the sleeve serves no electrical purpose?
2) In a second part of the project the directional driller is to install 4 - 3" HDPE sleeves in a common borehole, from a well house to a well vault pit for our electrical cables. We plan to install a shielded power cable assembly for the well pumps (2 conduit with a cable in each), a shielded direct burial instrumentation cable for the 4-20 mA signals in the pit and the final sleeve is for the float switches in the pit. The pit is a Class 1 Division 1 location. These switches are not explosion proof and must be powered through intrinsically safe barriers in a control panel. Our interpretation of the NEC says the conductors from the control panel to the probes must be in a metal grounded conduit. We are wondering if we install a corrugated metal jacketed cable assembly with say 14 #14 gauge conductors, if this would meet the intent of the code.
3) Our final question is related to local disconnect for the well and product pump. The pits are below ground and aside from explosion proof are corrosive locations due to salt water being just below the surface. The well houses are about 150' away from the well pits. The motor starters for the pumps are capable of being locked in the open position. We are in NYC and are governed by the 1999 NEC. Our question is are local explosion proof disconnect required in the vaults?
Thanks in advance for everyone's help.
Stu
My questions relate to installation of cables in directionally drilled conduits. For those of you who are unfamiliar with the technique it basically a horizontal drilling method in which a bit is pushed underground and conduit (usually HDPE - High Density Polyethelene) is pulled back in the borehole and used as a sleeve.
In our area, most of the time directional drilling is used for water, gas lines, and utility primary/secondary cable. The sleeves are usually roll out HDPE and vary in size from 3" to 18" which are fused to join the lengths. Our questions relate to the installation of electrical cables in these sleeves. The HDPE has no U/L listing as electrical conduit. The utility usually install their primary and secondary cables since they are not concerned with the NEC and U/L.
1) We are wondering if we install a cable or cable assembly (i.e. 3 conductor with ground shielded cable assembly similar to Coreflex) which is rated for direct burial can we install it inside the HDPE sleeve since the sleeve serves no electrical purpose?
2) In a second part of the project the directional driller is to install 4 - 3" HDPE sleeves in a common borehole, from a well house to a well vault pit for our electrical cables. We plan to install a shielded power cable assembly for the well pumps (2 conduit with a cable in each), a shielded direct burial instrumentation cable for the 4-20 mA signals in the pit and the final sleeve is for the float switches in the pit. The pit is a Class 1 Division 1 location. These switches are not explosion proof and must be powered through intrinsically safe barriers in a control panel. Our interpretation of the NEC says the conductors from the control panel to the probes must be in a metal grounded conduit. We are wondering if we install a corrugated metal jacketed cable assembly with say 14 #14 gauge conductors, if this would meet the intent of the code.
3) Our final question is related to local disconnect for the well and product pump. The pits are below ground and aside from explosion proof are corrosive locations due to salt water being just below the surface. The well houses are about 150' away from the well pits. The motor starters for the pumps are capable of being locked in the open position. We are in NYC and are governed by the 1999 NEC. Our question is are local explosion proof disconnect required in the vaults?
Thanks in advance for everyone's help.
Stu