If going residential cord and plug, most level 2 chargers want a 50A receptacle just like a residential range plug. Car chargers are continuous loads. So a 50A receptacle will allow configuring the charger for 240V 40A. There is no specific demand factor, so three of these would be a 150A load. If adding this on to a typical dwelling load, you would most likely get to apply the 0.4 factor that goes to all loads over the 10kw threshold except for hvac. So 3 chargers would increase the load calc by 60A.