electrical code 110.26(f)(1) a through d

Status
Not open for further replies.

rberg

New member
electrical code 110.26(f)(1) a through d

Need clarification regarding electrical dedicated space. We build pumping systems which include an air receiver, pumps and an electrical control panel. The vacuum pumps on mounted on top of the receiver and the electrical panel for the pumps is mounted below. The motors from the pumps sit slightly over the control panel. The code states piping, duct leak protection apparatus or othr equiment foregin to the electrical installation shall not be located in this zone. We do not conside the pump motors foreign equipment as they are directly wired to the panel. Does this configuration meet code?
 
Re: electrical code 110.26(f)(1) a through d

Re: electrical code 110.26(f)(1) a through d

The NEC does not really cover factory assembled equipment. You might get some arguments on that from other members, but as long as you are not doing something unsafe, I would not be too worried about it.

Your equipment might well be more appropriately covered under NFPA79 rather than NFPA70 (NEC).
 