Most standard shore power receptacles for RV"s are 30 amp 125v or 120/240v 50 amp non-gfi protected outlets, unless your under the new code requirements.
If an ATS was not in play, and you simply unplugged one of these cords (That fed the panel in the concession stand) from the generator and plugged it into one of these standard non-gfi protected receptacles, they would not trip.
Since your indicating that when plugging into shore power it would "Trip the GFI", then, I'm assuming your talking about plugging the feeder cable to the concession stand into a "Shore Power" 120v GFI protected outlet, or, using some type of 30a 125v or 50a 125/240v adapter to be able do so.
JAP>
Regardless if there is gfi protection of a receptacle that this would plug into, it is still a mobile piece of equipment that contains a sub-panel and there-fore the neutral and grounds need to be separated unless the power being supplied is provided onboard.