Hey guys,
NEC 230 States "Overhead service conductors must maintain a clearance of 3 feet from doors, porches, balconies, ladders, stairs, fire escapes, windows that open, or similar locations [230.9]. However, you don't have to maintain the 3-foot distance for conductors that run above a window."
From the attached picture, I am planning to run 4 sets of 3" IMC conduits between the 2 glass windows marked, which comes from the roof. Does NEC 230 apply for this? or is there any other code that calls for such clearances?
Thanks
NEC 230 States "Overhead service conductors must maintain a clearance of 3 feet from doors, porches, balconies, ladders, stairs, fire escapes, windows that open, or similar locations [230.9]. However, you don't have to maintain the 3-foot distance for conductors that run above a window."
From the attached picture, I am planning to run 4 sets of 3" IMC conduits between the 2 glass windows marked, which comes from the roof. Does NEC 230 apply for this? or is there any other code that calls for such clearances?
Thanks