Electrical conduits go through fire riser room

Status
Not open for further replies.

anbm

Senior Member
Location
TX
Occupation
Designer
Can electrical conduits run from one panel, pass through the fire riser room to feed another panel? Are there any code issues?
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
Firestopped is the more correct term, my mind is on woodworking recently.
Look at products from STI, Hilti, or 3M. It will be a system listed for the wall and raceway type, with a label that goes by the penetration for the building official.
check with your wholesale house for what they have access to.
 

tom baker

First Chief Moderator & NEC Expert
Staff member
Location
Bremerton, Washington
Occupation
Master Electrician
I would also check with the building AHJ on your application if it will be allowed
 
Last edited:
Status
Not open for further replies.
Top