domeng

Member
Does the NEC require a single protection device for conductors connected to the seconndary side of a transformer serving a power panel within 10 feet of each other
 
Does the NEC require a single protection device for conductors connected to the seconndary side of a transformer serving a power panel within 10 feet of each other
The NEC requires conductors to be protected per Article 240 and in your case particularly 240.21 (C).
 