First time posting here so please take it easy on me.
I am a building owner and project manager on a project where we are turning an old fire hall into 9 apartments. I have a great electrical contractor who has done rough in and everything has passed up until this point. I also have a full set of engineered drawings including the Electrical engineering. The problem is that there was a miscommunication between myself and the Electrical contractor about who was purchasing the main electrical equipment coming into the building. It was most likely my bad but regardless why I am posting and am scramble mode to find somewhere to source the equipment I need in a timely manner.
The load calc for the electrical is 308A not including the house panel and it only has house lights, a 115V recirc pump and 2 washer and dryers that are both gas dryers. Most of the stuff is ran on natural gass and I have high seer mini splits providing my heating and cooling throughout. Small studios and 3x 2 bedroom apartments are what are going in the building. I just wanted to put that out there so you understand why the low load calc. Here is what the Note is on my drawings that show what the electrical engineer spec'd.
1. Meter center shall have Nema 3R Enclosure Rated 42,000 AIC Containing 1-400/2 Main Breaker and 10-100/2 Tenant Breakers with utility Meter Sockets. Unit Shall be similar and equal to Siemens "Power Mod" style residential Meter Stacks.
Unaware of there being a shortage on meter banks or this equipment I was shocked when the supplier said there would be over a year delay on getting this equipment. They proposed an alternative to see if the electrical inspector would accept as the alternate route material would be "in stock". Her alternate plan was to do a trough with 10 individual meters and disconnects off of a single 400A disconnect. He was ok with that but when I got the quote for this " in stock" material was 4 months for some of the components.
I am behind the 8 ball here and looking for any suggestions or ideas as to either a) where to get something similar to what the electrical engineer spec'd or b) an alternative and where I might find a supplier who would have that alternate material in stock or a more reasonable lead time. One note I do have a 4 gang meter box that we took out of the building that both my electrician and electrical inspector said I could use.
Thanks for any help anyone can provide or suggest.
I am a building owner and project manager on a project where we are turning an old fire hall into 9 apartments. I have a great electrical contractor who has done rough in and everything has passed up until this point. I also have a full set of engineered drawings including the Electrical engineering. The problem is that there was a miscommunication between myself and the Electrical contractor about who was purchasing the main electrical equipment coming into the building. It was most likely my bad but regardless why I am posting and am scramble mode to find somewhere to source the equipment I need in a timely manner.
The load calc for the electrical is 308A not including the house panel and it only has house lights, a 115V recirc pump and 2 washer and dryers that are both gas dryers. Most of the stuff is ran on natural gass and I have high seer mini splits providing my heating and cooling throughout. Small studios and 3x 2 bedroom apartments are what are going in the building. I just wanted to put that out there so you understand why the low load calc. Here is what the Note is on my drawings that show what the electrical engineer spec'd.
1. Meter center shall have Nema 3R Enclosure Rated 42,000 AIC Containing 1-400/2 Main Breaker and 10-100/2 Tenant Breakers with utility Meter Sockets. Unit Shall be similar and equal to Siemens "Power Mod" style residential Meter Stacks.
Unaware of there being a shortage on meter banks or this equipment I was shocked when the supplier said there would be over a year delay on getting this equipment. They proposed an alternative to see if the electrical inspector would accept as the alternate route material would be "in stock". Her alternate plan was to do a trough with 10 individual meters and disconnects off of a single 400A disconnect. He was ok with that but when I got the quote for this " in stock" material was 4 months for some of the components.
I am behind the 8 ball here and looking for any suggestions or ideas as to either a) where to get something similar to what the electrical engineer spec'd or b) an alternative and where I might find a supplier who would have that alternate material in stock or a more reasonable lead time. One note I do have a 4 gang meter box that we took out of the building that both my electrician and electrical inspector said I could use.
Thanks for any help anyone can provide or suggest.