Re: electrical ghosts
What are the voltages of the other phases when a load is applied?
Has there been any noticeable lights getting brighter/dimmer?
Do you have a DVM/Amp-Probe with peek reading and hold feature?
The only way to diagnose a problem like this is having the proper equipment and the know how to operate it. Most utilities will install a special meter that monitors power quality and will give you a readout after 48hrs which might give you some incite as to which side of the meter it might be coming from but don't expect a miracle, as many times it can be from branch circuit wiring or a problem in the panel even a loose buss bar. Without PQ monitoring equipment it's hard to see whats really happing. Something is just not making any sense.
With your Amp-Probe try to see what the start up current is on the saw. It can't be the 10 amps you posted? What are your phase to neutral voltages? what are your phase to phase voltages? unloaded and after loaded.
Try to un-balance the panel by only turning on single pole breakers to a known resistance load on one phase of the panel only, then measure the voltage to see if it goes low while the other phase go high.
If it does then it is a bad neutral connection. To see a intermittent loose connection a true RMS meter will not show it, but a peek reading meter will.
It's to fast sometimes for the dampened meter (RMS) to show it. I've had this problem a few times and the POCO would only use the RMS setting on their meter, which would not show the fast fluctuations of the loose connection.
What are the voltages of the other phases when a load is applied?
Has there been any noticeable lights getting brighter/dimmer?
Do you have a DVM/Amp-Probe with peek reading and hold feature?
The only way to diagnose a problem like this is having the proper equipment and the know how to operate it. Most utilities will install a special meter that monitors power quality and will give you a readout after 48hrs which might give you some incite as to which side of the meter it might be coming from but don't expect a miracle, as many times it can be from branch circuit wiring or a problem in the panel even a loose buss bar. Without PQ monitoring equipment it's hard to see whats really happing. Something is just not making any sense.
With your Amp-Probe try to see what the start up current is on the saw. It can't be the 10 amps you posted? What are your phase to neutral voltages? what are your phase to phase voltages? unloaded and after loaded.
Try to un-balance the panel by only turning on single pole breakers to a known resistance load on one phase of the panel only, then measure the voltage to see if it goes low while the other phase go high.
If it does then it is a bad neutral connection. To see a intermittent loose connection a true RMS meter will not show it, but a peek reading meter will.
It's to fast sometimes for the dampened meter (RMS) to show it. I've had this problem a few times and the POCO would only use the RMS setting on their meter, which would not show the fast fluctuations of the loose connection.