Electrical NEMA rating for installation in ESFR

Status
Not open for further replies.
I would appreciate any hints on requirements for NEMA rating of electrical equiment/devices/lights/raceways in buildings/areas with Early Suppression Fast Response (ESFR) sprinkler system.
 

petersonra

Senior Member
Location
Northern illinois
Occupation
engineer
why would the type of sprinkler system make any difference?

the sprinkler is there to protect the building from burning down. if it happens to damage some equipment along the way, that is just too bad.
 

muskiedog

Senior Member
Location
Minnesota
No other requirements needed.

No other requirements needed.

No. We installed one in opur printing distrabution center. It does not require any changes. It works by dosing the effect area instead of drenching the whole building. Usually only 12 heads will go off at one time.
 