electrical noise
Mother Earth has a very low high-frequency impedance, AM radio station's antennas depend on it (one half of the antenna is the ground). But making a low impedance ground is a big problem. The antenna ground is up to several thousand feet of copper wire buried in a radial pattern from the antenna base.
so, then, using ground rods to elimanate noise could actually work depending on the noise that is causing the problems ? I wonder what the cut off frequency is for using the earth as a filter, and if its ever useful for the type of noise that generally causes problems with electronic equipment ?
Probably not!
a) There is a whole lot of difference between a 3000 foot ground system and an 8 foot ground rod.
b) The earth ground is not a major factor in noise problems. The noise current will not just flow into the earth and go away. Earth only enters the equation when the noise current can't find a better path back to it's source.
Interesting Discussion
When trying to lower noise levels we are trying to reduce the impedance between the source of the noise and its return path.
A zero potential ground plane being the ultimate goal.
Whatever can lower the impedance between source and the return path will help in theory. So I believe that ground rods can help, at least in theory.
We always attempted to lower the (ground) return impedance by using thick flat braided wire connected to building steel where possible. As a supplemental high frequency return path.
Here is an interesting link that speaks to the question about the conductance of the earth with frequency.
http://soil.scijournals.org/cgi/content/full/68/5/1515
If you want to skip ahead to the conclusion there are some good graphs there.
Many people tend to think only of the low frequency paths (60hz) and fail to consider that electrical noise is often a high frequency event.
. how does this remove noise from the lines?
Studies by the EPRI have shown a ground rod such as you describe can introduce more noise, or current (lighting) into the equipment as it creates a voltage drop from the ground rod to the main electrical ground, voltage drop = current flow.
I had the study and sent it to mike holt. He mad a graphic out of it in his grounding text