I'm not sure what a panelboard is that electrofelon referenced but that sounds like something I should look into. If that lets you customize the main breaker vs the busbar, it sounds like it would work.
You will not find a 200 amp panel with a 250 amp bus so forget that.... I imagine you can get a 400 amp main lug panel and get a 200 amp main breaker kit....
For Siemens, these will be bolt on only. There is another discussion going on right now about square D panelboards, and I believe those will take both plug on or bolt on.That is new to me however the cost will probably be much higher than the load centers.
Are the breakers standard style or bolt in? @electrofelon
Some thoughts...
There is a Siemens 'solar ready' panel that has a 100A 'parallel energy source' auxiliary service disconnect, but it's not compliant with the 2020 code, so if that's a deal killer...
Alternatively, numerous manufacturers make a meter main with a 225A busbar and a max 200A breaker, allowing you a 70A PV breaker, which is 56A of inverter output, or 13.44kW at 240V. Is that really not sufficient for a 16 or 17kW DC solar system? That's between 1.26 and 1.19 DC to AC ratio which is totally industry standard. You may not get enough extra production with more inverter power to justify the cost of a higher rated panel.
Or is you 16-17kW PV an AC output rating?
Based on some recent factory order panelboards I got, I would bet around $700-800 for a 250A buss with a 200 amp MB, including about 30 branch breakers. True panelbaords are super nice, but definitely cost more.The panelboard seems to be the way to go I just have no idea how much extra it will cost. I'm currently trying to get that info from a local supplier.
You dont always have to comply with 120% rule,I'm in the planning process of a solar install at my house. I'm planning on installing a PV system of about 17-18 kW. I'm trying to figure out the most economical way to satisfy the NEC 120% rule at the main panel. I was planning on replacing the main panel anyway because I've been doubling up breakers and am out of slots. My current panel has a 200 amp breaker and a 200 amp rated busbar. I thought a good solution would be to find a main breaker panel with a 200 amp main breaker and a busbar rated for over 250 amps. I tried looking for electrical panels with 250 or 300 amp busbars but haven't found any yet. It seems that most panels cap out at around 225 amps. I'm not sure if the best option is to look for a 400 amp panel and install a 200 amp breaker in it. I'm trying to get ahold of Eaton tech support but haven't heard back yet. I was wondering if someone else has run into this and has already found a solution. I briefly looked at installing 400 amp service but that was extreme overkill and quite expensive. Thanks.