Electrical Room Fire Rated Construction
twada
If an electrical room doesn't contain 112.5 KVA transformers, do the walls need not to be the fire rated? Or do all electrical room need to be constructed with fire rated walls?
Re: Electrical Room Fire Rated Construction
Any dry transformer that is enclosed except for ventilating openings does not need a fire rated room or vault unless these conditions apply:
1. The building is of a contruction type where fire rated electrical rooms are required. Unfortunately, the NEC ( NFPA ) building type does not correspond to BOCA yada yada.
2. The transformer needs to be cut off from flammable vapors, flammable dusts, dusts that would plug up the transformer ventilation yada yada.
3. The dry transformer is over 35,000 volts phase to phase. Dry transformer technology goes all the way up to 46,000 volts and fully hardened against lightning.
I have also put 4x4 wooden sleepers underneath a 27 KVA transformer both to keep it from being pushed too close to the wall and to double the lower front ventilation opening. Maybe somebody would want fire treated wood or steel sleepers but my interpretation of NEC is that the transformer is listed for direct mounting on a wooden floor. If the ventilation is great enough then any heat that radiates down through the ventilation openings would be overwhelmed by the air going up.
MC5W do you own a code book?
You should really look things up and stop shooting from the hip, of course that is just my opinion. :p
450.21(B) Over 112 1/2 kVA. Individual dry-type transformers of more than 112 1/2 kVA rating shall be installed in a transformer room of fire-resistant construction. Unless specified otherwise in this article, the term fire resistant means a construction having a minimum fire rating of 1 hour.
There are some exceptions for Class 155 or higher insulation systems.
Thats is fine for the NEC, however don't do that in a building type that is of resistant construction.
[ May 20, 2005, 03:58 AM: Message edited by: iwire ]
Originally posted by sandsnow:
Originally posted by ryan_618:
No, unless the building is type "A" construction.
What is Type A? We're still on the '97 UBC.
"A" is the IBC's way of saying fire rated. Type V-A for example is the equivalent of the UBC Type V-1hr. while Type V-B is the equivalent of Type V non rated, and so on through all of the construction types.
The transformer with wooden sleepers underneath was in a factory with concrete floors, concrete block walls, and a SPRINKLER SYSTEM.
I have never seen a dry transformer over 112.5 KVA that had less than 220 degree Celsius insulation.
Iwire, you did not quote the exceptions that I listed below my statement about dry ventilated trnasformers.
According to General Electric's installation instructions a dry ventilated transformer that is at full load will have a surface temperature of 90 degrees Celsius. That is more than hot enough to cause 2nd degree burns. Fortunately, many people only use 1/4 to 1/2 of their electrical system. If it was the kind of place where they really do use 3/4 or more of their electrical system the transformer needs to be behind a fence or better.
The only instances I know of where a dry transformer caught on fire wer over at International Exposition Center when running the indoor amusement park. The amusement park outfit thinks that 240 volts is somehow safer that 480 volts which is pure B.S. according to people who have died from contacting 120 volts. In this case the 480 volt primary taps of 120Y208 volt transformers were set to produce a secondary voltage of about 230 volts. That pushed too much magnetism through the core causing the core to overheat.
Interestingly enough, British coal mines have not had an electrocution since 1964 and they have 1,100 volt and 3,300 volt extension cords. So, if 3,300 volts is a safe voltage, how come 480 volts is not a safe voltage?
[ May 26, 2005, 04:25 AM: Message edited by: mc5w ]