Re: Electrical Room Fire Rated Construction
The transformer with wooden sleepers underneath was in a factory with concrete floors, concrete block walls, and a SPRINKLER SYSTEM.
I have never seen a dry transformer over 112.5 KVA that had less than 220 degree Celsius insulation.
Iwire, you did not quote the exceptions that I listed below my statement about dry ventilated trnasformers.
According to General Electric's installation instructions a dry ventilated transformer that is at full load will have a surface temperature of 90 degrees Celsius. That is more than hot enough to cause 2nd degree burns. Fortunately, many people only use 1/4 to 1/2 of their electrical system. If it was the kind of place where they really do use 3/4 or more of their electrical system the transformer needs to be behind a fence or better.
The only instances I know of where a dry transformer caught on fire wer over at International Exposition Center when running the indoor amusement park. The amusement park outfit thinks that 240 volts is somehow safer that 480 volts which is pure B.S. according to people who have died from contacting 120 volts. In this case the 480 volt primary taps of 120Y208 volt transformers were set to produce a secondary voltage of about 230 volts. That pushed too much magnetism through the core causing the core to overheat.
Interestingly enough, British coal mines have not had an electrocution since 1964 and they have 1,100 volt and 3,300 volt extension cords. So, if 3,300 volts is a safe voltage, how come 480 volts is not a safe voltage?