Looking for codes to help justify to a state run facility why they can't use an electrical room(room has multiple transformers and panels)as an office and have an employee working in there on a daily basis. So far I have come up with these codes from the 2017 NEC.
110.26(A)(4) Limited Access
Table 110.26(A)(1) Working Space
110.26(B) Clear Spaces
110.26(E) Dedicated Equipment Space
Can you think of any others?