Electrical room

Status
Not open for further replies.

jim dungar

Moderator
Staff member
Location
Wisconsin
Occupation
PE (Retired) - Power Systems
I am not suggesting. I am asking is their any such rule in nec 2017 version.
The NEC does not define nor require an electrical room, therefore it has no rules for one. I have seen switchgear install on production floors with bollards to protect it from forklift trucks.
 

retirede

Senior Member
Location
Illinois
I could see where a hotel might not want a server from the bar to be able to inadvertently flip a breaker off that would affect other areas of the facility, but that’s a design issue, not code.
 

hhsting

Senior Member
Location
Glen bunie, md, us
Occupation
Junior plan reviewer
I could see where a hotel might not want a server from the bar to be able to inadvertently flip a breaker off that would affect other areas of the facility, but that’s a design issue, not code.

Actually NEC 2017 section 240.24(b) first paragraph does require breaker to be ready access but there are no exception for branch circuit breakers ready access to occupant in bar in hotel.

So in a way it is code issue. Code says to do it regardless.

Now designer could have given panel that feeds space branch circuit at tenant space and feeder feeding that panelboard if iwner didnt want server to mess around. He didnt do this is a design issue not code issue.
 

paulengr

Senior Member
The NEC does not define nor require an electrical room, therefore it has no rules for one. I have seen switchgear install on production floors with bollards to protect it from forklift trucks.

See 110.21(B). 110.27(C) and 110.34(C). But also note that it says exposed, live parts. So if you have open, live bus bars or transformers with accessible bushings and similar live, open gear, it needs signs and protection such as locked or bolted gates, doors, etc. it also requires lots of danger signs. All this should be pretty obvious. Again think outdoor overhead substation. This is very different from where all the equipment is closed and normally locked, bolted, or interlocked. I have always interpreted the “licking” requirement as requiring some kind of tool for access…wrench, screwdriver, or key. No Codes come right out and say it that way but that’s the end result. I recognize that a screwdriver or key is a pretty low standard but that’s what it is. Locks are for honest people. I’ve witnessed multiple accidents and would be accidents from dishonest people. All I can say is criminals are stupid or they wouldn’t be criminals.

So no I don’t recommend licking MOST electrical rooms or covering them with danger signs on the doors,
 