Thanks-I guess I need to restate my situation. There is a contractor in my area who wants to use several 1st year apprentices for a utility solar installation (500 acres). I am the training director and will not be on the job. I have concerns about the apprentices building a fire in their hands since voltage will be present and they might be put into a bad situation which I want to avoid. I am wanting to develop a plan since I have concerns that the contractor is way over their head and I want to make sure that someone doesn't end up in the burn unit. Thanks
I hear you. I'm not so concerned about them being 1-year apprentices but I'm concerned about how you describe the contractor.
No way I can lay out a whole plan for you here but if I were you I'd emphasize these three things in addition to PPE and whatever else.
First, drill into these apprentices that any given string of modules are only connected to each other,
not to any home run wiring, until the proper time and procedure for connecting strings to combiners or whatever. (Good idea to tag out the ends of prepared strings and home runs when they're ready.)
Second, push the contractor hard to have a detailed, written, and organized procedure for connecting the strings in parallel at combiners or wherever. I think PPE for that part is totally appropriate. Not something the first years should be doing without supervision.
Third, make sure they include testing for polarity and ground faults on each string as part of the procedures.
An individual string is very unlikely to send someone to the burn unit, even if they forget to use PPE. The potential dangers involve lots of parallel strings being connected in a short circuit because something got reversed or faulted through being disorganized.