rozana81
Member
- Location
- keller, tx
Looks like some of the jurisdiction requires both meter disconnect and service disconnect. But my question is if the meter disconnect is turned off, would that not kill power to the building? Why do we need another disconnect after meter?
View attachment 2571193
Thanks David! So, why do you need another disconnect switch after the meter and before the panelboard too?the service disconnect has not been required outside.
here if it is 480/277 AND the meter is line voltage not CT. the utility requires a disconnect ahead of the meter.
here they do not care if it is fusible or not they just want the meter cold before they set it or pull it
Sent from my SM-S901U using Tapatalk
You would be hard pressed to find an un-fused disconnect that has an adequate short circuit rating much higher than 5kA, so in many services, it needs to be fused, just to get an adequate SCCR.if I was doing it, the disconnect ahead of the meter would be un fused eather way its not the service disconnect
the service disconnect is outside in your picture. it could have been inside.
Eather way the NEC requires the service disconnect, the utility required the isolation switch.
Sent from my SM-S901U using Tapatalk
Thanks David! So, why do you need another disconnect switch after the meter and before the panelboard too?
Mayhaps because the service feeds multiple tenants, so they need a way to de-energize one meter without having to de-energize them all.So, why do you need another disconnect switch after the meter and before the panelboard too?
it is feeding just one tenantMayhaps because the service feeds multiple tenants, so they need a way to de-energize one meter without having to de-energize them all.
Then what are the trough and the large switch to the left, and whatever that is on the right, for?it is feeding just one tenant
To me, that's the feeder going up. (technically, it doesn't change the question)Is the conduit going up the wall from the higher switch the service conduit or is the service in the wireway ??
did a quick look at utility req. 480/277 volt 400 amps or less line voltage meteringYou would be hard pressed to find an un-fused disconnect that has an adequate short circuit rating much higher than 5kA, so in many services, it needs to be fused, just to get an adequate SCCR.
Still a lot of unknown facts... I though perhaps the service conductors were in the wireway with one set metered out of sight and feeding the two disconencts and one set feeding the meter shiown..... but comjectureTo me, that's the feeder going up. (technically, it doesn't change the question)
In my area the meter disconnect is sealed by the utility and not suitable for used as a service disconnect, because you need a tool to cut the seal to operate the switch.Thanks David! So, why do you need another disconnect switch after the meter and before the panelboard too?