Electrical service configuration

jap

Senior Member
Occupation
Electrician
The only reason I don't think the disconnect after the meter is fused where it would turn into a feeder is because I don't see any raceways coming out of it for the grounding and bonding to take place.

This seems to be a disconnect ahead of the meter for the power company's use that may or may not be sealed by them , and, a customer side
disconnect for the service conductors for an outside emergency disconnect.

If the utility power is coming in from the bottom that is.

JAP>
 
Last edited:
Location
mississippi gulf coast
Occupation
Electrical Contractor
can i ask a question without generating a new thread? i'm putting a service on a house 600 disconnect outside, wanting to feed 3- 200amp main breaker panels through a trough on other side of the wall. would i be within code to come off the disconnect with 3 sets of 250mcm al and feed each panel with 1 set and no other over current protection?
 