D Djelite Senior Member Location Ny Occupation Electrician Apr 19, 2022 #1 Im i right when i say that the nec requires a sleeve to be placed between walls ceilings and floors for any conduit penetrations but the ul white book advices against this?
Im i right when i say that the nec requires a sleeve to be placed between walls ceilings and floors for any conduit penetrations but the ul white book advices against this?
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 19, 2022 #2 No, the NEC has no say in the matter. Roger
roger Moderator Staff member Location Fl Occupation Retired Electrician Apr 19, 2022 #3 You should look into the UL Orange Books. AKA The Fire Resistance Directory Roger
J Jake@01 Member Location Port Angeles wa Occupation Journeyman Electrician Apr 19, 2022 #4 I agree & don't believe the NEC has any regulations regarding this topic. Sent from my SM-S906U using Tapatalk
I agree & don't believe the NEC has any regulations regarding this topic. Sent from my SM-S906U using Tapatalk