We have an Outdoor motor starter panel that houses all controls and starters for two 480V/3ph motors and twelve 480V/3ph motorized valves.
The panel is 7FT tall
The best place to this panel is on a wall that has a 6" Air Header Pipe mounted 9FT above the floor.
Directly above the pipe is steel grating for a walkway.
110-26.1.(3)(e) says this is okay for height and headroom.
110-26.1.(3)(f)(1) does not apply, because it is not inside.
110-26.1.(3)(f)(2) refers back to work space and we are okay there.
Asking for confirmation and to see if I need to look in another section?