Ainsley Whyte

Senior Member
Location
Jamaica
Occupation
Senior Electrical Engineer
Greetings all,

Can anyone share space requirement when building substation and and fire detection requirements, voltage that will be in substation are 13.8KV, 480V and 4160V.


Thanks
 
Is this application under the scope of the NEC or is it a utility installation?
If NEC, 110.16 is where you start, and then to part III of article 110. Best if you read for yourself.
Fire detection is per a different NFPA document, the NEC covers the wiring, not the placement or whats required.
 