Electrical switchgear bus energization only

Location
Ras tanura
Occupation
Electrical inspector
If all SAT activities for an MV switchgear have already been completed and the plan is to energize it in phases as follows:

Phase 1: Only the incomer breaker is closed. The busbar is energized (highlighted in red), while all outgoing feeders are isolated (open and racked out, shown in gray).

Phase 2: Each outgoing feeder is individually racked in, closed, and energized only after its specific energization package is approved and executed. This powers its downstream load (e.g., a transformer or motor).

Considering that all tests related to both incomer and outgoing feeders are already completed, is this phased approach to energization technically acceptable and safe?

1000187976.png
 
We stopped racking breakers on and off of energized busses.
We would do them all at once but still close and commission them individually.
 