Electrical tape or short wires.
Pinnie
Humble Disciple
Ohio
Commercial Electrician
Pretend a drywaller hit the wire far back on the wire to where if you cut it you would have less than 6 inches of wire from the back of the box (300.14). Would you prefer cutting them and pigtailing or wrapping with electrical tape. Also what is electrical tape rated for/ intended uses. We use it for all sorts of stuff obviously but what does code allow.
If the copper is not damaged, something that is very unlikely, I would use heat shrink. It would be very difficult to wrap the tape on a conductor that does not reach outside of the box.
  • Like
Reactions: J2H
Many common electrical tape products are rated for 600V and are fine for addressing minor damage to insulation where copper isn't damaged. But I agree with the other comments in this case.
300.14 doesn’t care if the 6” of free conductor is spliced or unspliced. So nut and crimp away!
I re-insulate wire with insulation stripped from a new piece the same gauge or one up, depending on fit.
This is useful on BX where the old insulation is crumbling away. I push it as far as I can into the sheath.