georgestolz said:
How quickly can you get to that OCPD without a key to the locked door?
What bearing does this question have on OPs question?
Quote:
240.24 Location in or on Premises.
(E) Not Located in Bathrooms. In dwelling units and guest rooms or guest suites of hotels and motels, overcurrent devices, other than supplementary overcurrent protection, shall not be located in bathrooms.
Sounds like you're Ok.
__________________
Trevor
What makes you think this is not a dwelling unit?
240.24(B) Occupancy. Each occupant shall have ready access to all overcurrent devices protecting the conductors supplying that occupancy.
Exception No. 1: Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the service overcurrent devices and feeder overcurrent devices supplying more than one occupancy shall be permitted to be accessible to only authorized management personnel in the following:
(1)
Multiple-occupancy buildings
(2) Guest rooms or guest suites of hotels and motels that are intended for transient occupancy
Exception No. 2: Where electric service and electrical maintenance are provided by the building management and where these are under continuous building management supervision, the branch circuit overcurrent devices supplying any guest rooms or guest suites shall be permitted to be accessible to only authorized management personnel for guest rooms of hotels and motels that are intended for transient occupancy.
What is Multiple-occupancy buildings?