aelectricalman Senior Member Location KY May 20, 2011 #1 Does anyone know if electrican2.com ampacity calculator figures in 125% for wire sizing for solar installation? or is that left for us to determine?
Does anyone know if electrican2.com ampacity calculator figures in 125% for wire sizing for solar installation? or is that left for us to determine?
Little Bill Moderator Staff member Location Tennessee NEC:2017 Occupation Semi-Retired Electrician May 20, 2011 #2 aelectricalman said: Does anyone know if electrican2.com ampacity calculator figures in 125% for wire sizing for solar installation? or is that left for us to determine? Click to expand... I'm not sure about solar, but in the OCPD and wiring calculator when you put in your continuous loads that takes the 125% into account.
aelectricalman said: Does anyone know if electrican2.com ampacity calculator figures in 125% for wire sizing for solar installation? or is that left for us to determine? Click to expand... I'm not sure about solar, but in the OCPD and wiring calculator when you put in your continuous loads that takes the 125% into account.