Curryb
Member
- Location
- Carson city
- Occupation
- Electrician
Hello I am installing a 400 amp meter main at the bottom of a driveway on a pedestal and feeding two 200 amp transfer switches up the hill at the house . I will have an electrode at the meter main but it is my understanding that I need an electrode at the house as well. I can not use the EGC in the feeder to serve that purpose. Some guys are saying I am wrong. After looking in article 250 section 3 seems I am correct but am wondering everyone’s opinion. In article 250.118 B 1 there is an exception saying you can use both for same purpose but I think I am confused. Thanks again for your input