I think it is worth noting that your photo is listed to be used for compliance with 250.94. The reason I mention this is that the 2014 NEC has clarified that the bonding bar installed for 250.94 cannot be used for connecting GEC conductors other than low voltage systems.
That said, I would have no issue with using this, as long as it complied for sizing, and you had a second one to comply with 250.94.
I did not know that. TY
250.94 Bonding for Other Systems.
If I ran a #4 through it to the metal water line continuous could it be used like a tap?