zemingduan
Senior Member
- Location
- Philadelphia,PA
- Occupation
- Electrical Designer

1. The conductor circled in above screenshot is bonding jumper instead of grounding electrode conductor according to the NEC definition. Do you size this conductor according to 250.66 or 250.102? I see many people size it according to 250.66 (B) and use #4 Cu. But I think per code it should be sized according to 250.102. And 250.102 requires it to be larger than 3/0 Cu depending on the incoming service conductors size.
2. When you bond the building steel to the concrete encased electrodes, the bonding jumper from building steel to the concrete encased electrodes shall follow the 250.102 and may be required larger than #3/0 Cu depending on the service conductor size. However the GEC from neutral to the building steel (not shown in the screen shot above but if we have one) follows 250.66 and is not required to be larger than #3/0 Cu. Why?
Besides when you connect the neutral conductor directly to the concrete encased electrodes, the GEC is not required to be larger than #4 Cu according to 250.66 (B).
I know they are code requirements, but i can not understand the logic/insight behind it. It doesn't make sense to me. Can someone explains it to me?
Thanks!