If I were to wire an office and it had all electronic ballast should I be concerned about using MWBC on these circuits? I assume electronic ballast are non linear-- Is that correct?
Most electronic ballasts have 10% or 20% Total Harmonic distortion. I think that would equate to only 10% or 20% of the load being harmonics.
So I think the answer is no.
Steve
So you are saying there is no reason to be concerned with a MWBC serving fluorescent lighting with electronic ballasts.
I think there is probably a lot more "efficiency" benefit from using MWBC's on lighting loads, since the lights are often left on all day and Lower voltage drop = less energy wasted.
Steve
Please feel free to question -- I would never consider that hijacking a thread-- little offshoots perhaps but it is fine with me...:smile:I don't mean to hijack the thread, but here goes..... Why would a MWBC result in lower voltage drop at the load?
I don't mean to hijack the thread, but here goes..... Why would a MWBC result in lower voltage drop at the load?
I will give this a shot. Others will be along to correct me.
Assume the loads are balance on two (240V 1ph) or three phases. The neutral would theoretically not be needed. Therefore less resistance in the circuit.
If I were to wire an office and it had all electronic ballast should I be concerned about using MWBC on these circuits? I assume electronic ballast are non linear-- Is that correct?
I'd be wary of doing MWBC with electronic ballasts..even though the percentage isn't bad enough to affect load calcs that much harmonic distortion would be bad..remember depending upon each ballast's THD, they may add, subtract and multiply at random. Which could cause wire heating and more likely ballast failures.
Bid a bit more to cover the extra copper costs and avoid a lot of callbacks to change ballasts.![]()
If there is no return current the resistance does not matter. If it does not return via the neutral it still has to return tto the 'other' phase so it will contribute to the voltage drop through the path it takes.
There is no free lunch, what goes up must come down and all energy is already created in the Universe it just keep converting from one form to another, and so on and so forthings.......:grin:
Here is an illustration from Ed MacLarren that will help visualisation.
![]()
Roger
Interestingly, the EC told me that someone said that they make 12/4 MC with a #10 neutral for this purpose. Had never seen that or heard of it.
In my area MC is king. We can get MC in all sorts of sizes and combination.
Check out this catalog for tons of MC
http://www.afcweb.com/pdfs/afc_cable_catalog/AFC0706_Cbl Cat_pt1.pdf
I will give this a shot. Others will be along to correct me.
Assume the loads are balance on two (240V 1ph) or three phases. The neutral would theoretically not be needed. Therefore less resistance in the circuit.
iwire said:First there is no reason that MWBCs will cause ballast failures, none. (excluding open neutals)
Second lets be honest, you do not like MWBCs at all for any use.
To the first, I respectfully disagree with the statement of "none", as it would depend on if the ballast itself was sensitive to harmonics.
By the way, thanks for posting the diagrams on post #11, that is quite educational and a great find!!
The Current still travels "out" and "back",
just not "back" on the neutral.