20% 5th and still a PF of .95+? How does it do that?
When I said "ideal" I was including your BIG choke.
Tapatalk!
Pasting a table may not work....
540 Vdc
100 Adc
54 kW
81.6 Aac
400 Vac
56.6 kVA
0.955 pf
OK. Narrative version.
Take 400Vac and rectify it with a three phase bridge.
You get 540Vdc. (400*1.35)

Apologies - not best resolution. I used equation editor in Word to do it and then stuck it in photobucket. It is what it is.
Load it to 100Adc. So you have 54kW. (100*540/1000)
The input current is a 120deg rectangular pulse in each half cycle thus is 100*sqrt(2/3) or 81.6A
Input kVA is sqrt(3)*VL*IL/1000 = 56.6kVA
Defining pf as kW/kVA you get 54/56.6
which is >0.95
This is for level DC. That big choke again.
Clear as mud?